Achieving unity power factor through the use of synchronous condensers can be a win-win situation for power utilities and consumers.
This article continues my previous article on power factor (Pumps & Systems, April 2016, read it here), which prompted interesting responses from readers. Specifically, we will look at this question: What is a synchronous condenser, and what does it have to do with power factor?
Here is a quick review of power factor: Power factor is the factor by which apparent power, or kVA, is multiplied to obtain kW.
  • kW = Power Factor x kVA
  • Power Factor = Cosine of Angle = kW / kVA
Graphical representation of the power factor calculationFigure 1 (top). Graphical representation of the power factor calculation. Figure 2 (bottom). A diagram showing stator magnetic field rotation (Graphics and images courtesy of the author)
Power factor is a measurement of how efficiently you are using electricity. It is defined as the ratio of working power (kW) to total power (kVA). A power factor of 0.7 means that 70 percent of power supplied to a facility is being used efficiently and 30 percent is being wasted—and this waste often results in a higher utility bill.
Induction motors always absorb kilovolts of reactive power (kVARs) from the system. Synchronous motors have the ability to supply leading kVARs to improve system power factor.
Now we will discuss some viable solutions for improving power factor, specifically synchronous condensers.
A synchronous condenser—sometimes called a dynamic capacitor, synchronous capacitor or synchronous compensator—is, for all intents and purposes, a synchronous motor.
The only difference between a synchronous motor and a synchronous condenser is the synchronous condenser shaft is not connected to anything—it simply spins unimpeded.
The sole purpose of a synchronous condenser is to adjust conditions (power factor) on the electric power transmission grid.
Image 1. A 7,200-horsepower motorImage 1. A 7,200-horsepower, 20-pole, 4kV synchronous motor
How Does a Synchronous Motor Work?
As mentioned earlier a synchronous motor and condenser are one and the same. That being said, the diagram in Figure 2 shows conditions in a synchronous motor when operating in synchronism and at no load. When the motor is loaded, the rotor will drop back along Curve C, the curve of synchronous torque, sufficiently to develop the load torque.
Curve C is the resultant of magnetic reluctance torque, Curve A, and the definite polarity torque, Curve B. The maximum synchronous torque is reached at about 70 electrical degrees lag of the rotor.
components of a synchronous motorFigure 3. The main components of a synchronous motor include the frame, stator, rotor, exciter and amortisseur winding.
A synchronous motor has a three-phase stator similar to that of an induction motor. The unit starts as an induction motor using the amortisseur winding (see Figure 3) requiring slip to produce starting torque.
A rotating field (rotor) with the same number of poles as the stator is supplied by a source of direct current (DC). The rotor current establishes a north-south magnetic pole relationship in the rotor pole pairs, enabling the rotor to “lock-in-step” with the rotating stator flux.
Synchronous Motor as a Condenser
An overexcited synchronous motor (condenser) has a leading power factor. Increasing the condenser’s field excitation results in furnishing reactive power (vars) to the system.
In an industrial plant with a large number of induction motors, synchronous motors (condensers) can be used to supply some of the reactive power required by induction motors. This improves the plant’s power factor and reduces the reactive current required from the grid. The main advantage of a synchronous motor (condenser) is the ease with which the amount of correction can be adjusted.
Unlike a static capacitor bank, the amount of reactive power from a synchronous condenser can be continuously adjusted. Reactive power from a static capacitor bank decreases when grid voltage decreases, while a synchronous condenser can increase reactive current as voltage decreases.
Another benefit of synchronous condensers is their ability to control voltage levels. A synchronous condenser naturally supplies more reactive power to a low voltage and absorbs more reactive power from a high voltage, plus the field can be controlled as previously mentioned. The reactive power improves voltage regulation in situations such as starting large motors or in systems where power must travel long distances from where it is generated to where it is used.
The power generators would like their customers to present a load to the power grid as close to unity power factor as possible. Unfortunately, this is not happening given the number of induction machines. However, the utility is required to provide peak voltage and current in the wave form at any given time.
A power factor of less than 1 results in an increased cost to the power generator. Many utilities are passing this cost to their customers in the form of power factor correction charges. Therefore, achieving unity power factor through the use of synchronous condensers can be a win-win situation for both the power utility and the consumer.
To read more Motors & Drives articles, go here.