How to model a damper in a system simulation software tool as a control valve with an approximated flow coefficient profile.
01/14/2019
Editor’s Note: Jeff Sines is a member of Ray Hardee’s team at Engineered Software Inc. This month, he is a guest columnist in Hardee’s place.
A damper is used extensively in the heating, ventilation and air conditioning (HVAC) industry as well as other industries that move air or compressible gases for their processes. A damper controls air flow throughout a duct system to evenly distribute air or gas. It operates by changing the size and shape of its flow path, so its flow capacity (or conversely, resistance) changes with position. This column describes how to model a damper in a system simulation software tool as a control valve with an approximated flow coefficient (Cv) profile. A damper specification datasheet is used as an example in this column.
Some damper manufacturers provide performance curves for their products. An example performance curve graph of pressure vs. air velocity is shown on the next page for fully open dampers of 16 inches, 24 inches and 36 inches.
This performance curve has velocity units in feet per minute and pressure drop in inches of water gauge. Some manufacturer curves may be in other units such as cubic feet per minute (cfm). The system simulation software needs the flow coefficient (Cv or Kv) at different throttling percentages in order to model the damper as a control valve. The first step is converting a set of data points (velocity and pressure drop) for the fully open position to a Cv value. The equation from the Crane Technical Paper TP-410 to be used to obtain the Cv values is shown as Equation 1.
Equation 1
Cv = W63.3FPYxP'1ρ1−−−−−√Cv = W63.3FPYxP1'ρ1
The equation can be re-arranged:
Cv = W63.3FPYdPρ1−−−−−√Cv = W63.3FPYdPρ1
